Is it safe to use LR200 with Horn on Fermenter Tank with 9% alcohol content, 20 inH2O pressure and closed vessel? Thank you very much for your feed back |
| 12/1/2011 7:26 AM | |
|
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, Well, you have to study the manual and the local regulations. Have here 1 manual, there are lots more, don't know the exact type you have in mind. http://support.automation.siemens.com/WW/view/en/38741858 Have a close look at the Environmental part of it. Regards, Marcjan |
Last edited by: Marcjan at: 12/1/2011 7:28 AMProblem solved? |
|
| 12/3/2011 12:27 AM | |
|
Posts: 36 Rating:
|
Thanks |
| 12/12/2011 10:31 AM | |
|
Posts: 36 Rating:
|
Is it safe also use LR250 on same closed vessel 9% alcohol content, 20 inH2O pressure? Thank you so much |
| 12/12/2011 3:00 PM | |
|
Posts: 74 Rating:
|
Hi Again habella Sure it is. Just make sure you select the correct area electrical classification and heed the warnings I posted earlier. Note that 20" H2O pressure is less than 0.5 atm so you will not require a pressure rated version. This saves a few $$. Build your LR250 on the PIA Selector http://pia-portal.automation.siemens.com Cheers [ |:) |