(0)| 1/19/2012 10:48 AM | |
|
Joined: 12/13/2005 Last visit: 10/13/2025 Posts: 65 Rating:
|
Hello all, I have a IM151-8 PN/DP CPU. Is it possible to use it like a Profinet Master and let it communicate with some NON-Siemens profinet Slaves? So yes, I don't need to add an extra S7-CPU 3xx PN. |
| 1/23/2012 7:45 PM | |
|
Posts: 947 Rating:
|
Hello Mr. Q-Bridge IM151-8 can't work as profinet master. But you can use protocol UDP, TCP for connection. |
| 1/23/2012 11:46 PM | |
|
Joined: 10/7/2005 Last visit: 1/13/2026 Posts: 3054 Rating:
|
Dear all seems there's some conflicting advise here, I personally reside with Wizard's and will claim too that the IM151-8 CPU can defintely be used as a PN I/O Controller. Apart from having used it as such, it'stechnical specdoes also confirm this and I hope this helps. |
|
Cheers |
|
This contribution was helpful to
|
|
| 1/24/2012 5:28 PM | |
|
Posts: 1547 Rating:
|
Hello, I just want to confirm Wizard's and fritz's statement. The configuration is described in the manual |