(0)| 1/30/2012 1:28 PM | |
|
Joined: 11/9/2008 Last visit: 1/10/2026 Posts: 414 Rating:
|
Hi All, I want to establish communication between client CPU 313C over Profibus CP 342-5 and CPU 417-4H. I have connected GSD of CP 342-5 in my project to IM 153( 153-2BA81-0XB) and this IM is connected to CP 443-5 EXT (443-5DX04-0XE0/V6.0).I am using PCS 7.0 and both project configure differently so I want know which setting and communication block I need to use in my project as well as in his project or in my project Can I use Load and Transfer instruction to read/write the data.Please find the my Hardware configuration for your referance. Regards, Yogendra G.
AttachmentHW Settings.pdf (190 Downloads) |
| 1/30/2012 2:34 PM | |
|
Posts: 1121 Rating:
|
Hi Well you can use DP Send Recive block or Get Put blocks for communication between S7300 and S7400H system. FB14, FB 15 Get Put blocks FC1, FC2, DP_Send & DP_Recive. Please find the link for the same. Have fun.... |
Last edited by: Tagolover at: 1/30/2012 2:38 PM |
|
| 1/31/2012 5:51 PM | |
|
Joined: 11/9/2008 Last visit: 1/10/2026 Posts: 414 Rating:
|
HI Tagolover, Thanks for your reply I will try and if any problem I'll come to you. Regards, Yogendra G.
|