Is it possible to make a database connectionto an external mainframe with the KTP 600 Basic color? I know theHistorical Data function is disabled, if I use the KTP 600 Basic color device type in wincc Flexible 2008 SP3. Maybe I can do it like this? : Panel -> PLC database -> Mainframe I want tolog every alarmmessage that has been generated. So I can be able to monitor the alarms form the distance. Still being able to view the alarms with the Alarm View screen on the touchpannel. Also when there is a power failure, the alarm messages need to be reloaded in to the alarm view. So how can I load database info, from PLC database,back in to my Alarm view? Or do i need a SIMATIC HMI TP900 Comfort for this ? |
Last edited by: MKS02 at: 4/4/2012 11:36 AM |
|
| 4/4/2012 12:27 PM | |
|
Joined: 9/28/2005 Last visit: 12/9/2025 Posts: 2957 Rating:
|
Hi, You can't store historical data with Basic panels, so there is no option for you here, you need other type of the device. If you choose Comfort panel then please keep in mind that you can't use it together with WinCC Flexible. You need WinCC V11 (TIA portal) for that. If you chose device type which is capable of storing historical data then maybe this FAQ will be interesting for you How do you integrate an HMI operator panel into a local network? |
|
Best regards, |
|
| 4/4/2012 3:03 PM | |
|
Posts: 24 Rating:
|
Oky Thanks a lot! |