(0)| 9/17/2012 3:27 PM | |
|
Joined: 10/7/2005 Last visit: 1/23/2026 Posts: 3054 Rating:
|
Hello aag_03 while the IM308C can function as a DP Slave, it can only do so in a central rack in combination with an S5 CPU (i.e.it makesthat PLC function as an intelligent DP Slave). As such you can NOTuse an IM308C to convert an S5 expansion rack into a "pure" DP Slave I/O station. If you are not afraid to lookoutside the Siemens world, you can though use a IM306 DP Slave modulewhich willallow to do what you plan on doing. I hope this helps |
|
Cheers |
|
This contribution was helpful to
|
|
| 9/17/2012 11:42 PM | |
|
Joined: 10/7/2005 Last visit: 1/23/2026 Posts: 3054 Rating:
|
Yes it is dear aag_03 Don't worry that the IM306 manual (download is available HERE)mentions an S7 as the DP Master, it will work with any DP Master (including and IM308-C). You'll obviously need the GSD file for the IM306 DP Slave (download it from HERE)and configure the DP Slave in COM Profibus, but that's essentially it. I hope this helps |
|
Cheers |
|
This contribution was helpful to
|
|
| 9/18/2012 6:56 AM | |
|
Posts: 84 Rating:
|
Thank you very much, dear fritz! You saved me!!! This information will help to solve our problem |
This contribution was helpful to
|
|