Hello You put in the same slot was the CPU. If you need i can help you Nilton Junior |
| 12/12/2012 2:21 AM | |
|
Joined: 10/7/2005 Last visit: 1/14/2026 Posts: 3054 Rating:
|
Hello ryan cordova I think Jr_Jrsolution...misunderstood your question as your 6ES5700-2LA12is a Central Rack (CR) and you can NOT use the IM314 in it. The IM314 can only be used in ExpansionRacks (ER's) which would beeither an ER701-2 or ER701-3 in your 115U case (i.e. replaceyour CR with an ER if you have I/O cards in it thatrequire to be linked to an S7-400). Have a look at chapter 3.1.2 of the 115U manual as well as the How do I link an S7-400 with S5 expansion units? FAQ for more on this. I hope this helps |
|