hello is it correct to use PM230 IP20 for conveying application ? |
| 2/15/2013 3:28 PM | |
|
Joined: 10/11/2006 Last visit: 1/8/2026 Posts: 6065 Rating:
|
Hello, normally the PM230 is not designed for conveyors. Its for pumps and fans. At a conveyor there could be always some generatoric shares which could creates Vdc overvoltage at a PM230. Following an example with a G120D. But also PM240 would be a good solution. http://support.automation.siemens.com/WW/view/en/58399364 |
|