(0)| 5/6/2013 9:59 AM | |
|
Posts: 4620 Rating:
|
Hi Ashish, GSD file?or Firmware? |
Last edited by: Ste39 at: 5/6/2013 10:01 AM |
|
| 5/6/2013 10:39 AM | |
|
Joined: 2/6/2009 Last visit: 1/6/2026 Posts: 940 Rating:
|
Hi, The H-system CPU cannnot be communicated with any thierd party system directly since it contains two CPU. So you wont get GSD file for the CPU 412-5H. If you want to communicate the CPU 412-5H to any third pary system, you need to used theY-Link. Here is the linkfor Profibud GSD files of all Simatic components. |
|
_______________________________________________________________ |
|