(0)| 7/1/2013 8:28 AM | |
|
Joined: 8/25/2006 Last visit: 1/16/2026 Posts: 2221 Rating:
|
Hello. 2Q - 6RA8025-6DS22-0AA0 4Q - 6RA8013-6DV62-0AA0.
|
| 7/1/2013 4:32 PM | |
|
Posts: 378 Rating:
|
Dear KSN, Thanks for replay I have doubt since my motor is permanent magnet i dont have a place to connect the field output so if i connect armature supply and left the field output I guess i will have Field loss alarm with no operation. Is there any possiblity to disable field output? Regards |
| 7/1/2013 5:14 PM | |
|
Joined: 8/25/2006 Last visit: 1/16/2026 Posts: 2221 Rating:
|
Yes, you can disablefieldviaparameter. |