7/7/2013 7:05 PM | |
Posts: 559 Rating: (87) |
Please go through the below8 link: Which will help u to clear your fundamentals: /tf/WW/en/Posts/73946#top
|
7/9/2013 9:31 AM | |
Joined: 1/4/2007 Last visit: 5/23/2024 Posts: 1123 Rating: (174)
|
Hello @m!+, You need at least an adjustment weight of 5% of 22.5t (=3x7.5t) = 1.125t. That menas your 1250kg water are ok. But I don’t understand your procedure. You wrote: “2)Tank was empty. Carried out Adjustment zero valid Got Adj. digits 0=== 3730 Adj. digits 1=== 0 Accept and send => not necessary 3)Put 1250Kg water in tank and carried out Adj. Weight valid. Got Adj.digits 0=== 0 => Why do you have now 0 digits??? You must have the 3730 digits!!! Adj. digits 1=== 4972“ Please note: The adjustment digits must havea difference of at least 3000 digits! On the internet you can find the procedure how to do an adjustment with the Siwatool-software: http://support.automation.siemens.com/WW/view/en/37733600 Best regards Siwarexi |