(1)| 10/25/2013 2:53 PM | |
|
Joined: 9/27/2006 Last visit: 1/16/2026 Posts: 12481 Rating:
|
Hello Anas10; May I ask how familiar you are with Siemens' hardware, in general, not only with the ET 200S?Experience will teach you that "recommendations" from Siemens manuals and other documents are quite mandatory. If they "suggest" you use a termination module in the ET 200S configuration, be assured that you will get all kinds of ugly messagesof the sort you are recievoing if you try to bypass their use. Have a look at the following ling, and the attached image I have taken from there; it shows that a missing termination module will cause a defective configuration status in the ET 200S rack, which will provoque diagnostic buffer entries: SIMATIC ET 200S Distributed I/O IM151-7 CPU Interface Module |
This contribution was helpful to
|
|
| 10/28/2013 12:11 PM | |
|
Joined: 9/27/2005 Last visit: 12/16/2025 Posts: 203 Rating:
|
Hi, terminated module is mandatory. Greetings Morten |