(0)| 1/8/2014 10:44 PM | |
|
Posts: 895 Rating:
|
... what value has p2000? which HEX value do you send at high speed? - maybe p2000 = 1500rpm und you send for 3000 rpm 7FFF and then 8000 HEX? |
| 1/9/2014 6:23 AM | |
|
Joined: 1/23/2012 Last visit: 11/6/2025 Posts: 33 Rating:
|
Dearzako_, Thank you very much . The value in P2000 is 1500 The value i send for the 3000 RPM is 32768 (8000) that's the problem . Now it ok . If possible pls tell me the how we can disable the Negative value or disable the reverse direction in the Inverter . For my application the motor should not run in the reverse . Regards, Arunram Vasudevan |
| 1/13/2014 9:13 AM | |
|
Joined: 1/23/2012 Last visit: 11/6/2025 Posts: 33 Rating:
|
Dear Zako , thank you very much for the inforamtion.. :) Reagards, Arunram Vasudevan
|