Hello Jey; Paramater RECORD (datatype ANY): Target area for the diagnostics data read. Only the BYTE data type is permissible. The minimum length of the data record to be read or the target area is 6. The maximum length of the data record to be read is 240.Example: if you want to save the diagnostic data (65 bytes) recovered from your slave in DB82,using bytes 0 to 64 of DB82, then your RECORD parameter should be: Record:= P#DB82.DBX0,0 BYTE 64
|
Last edited by: dchartier at: 7/23/2013 7:09 PMLast edited by: dchartier at: 7/23/2013 7:08 PM |
|
This contribution was helpful to
|
|
| 7/24/2013 1:00 PM | |
|
Joined: 8/1/2008 Last visit: 1/16/2026 Posts: 40 Rating:
|
Hi dchartier
thank you forinformation. I understood. Best regards, jey |
| 4/13/2014 11:29 PM | |
|
Joined: 9/1/2005 Last visit: 1/9/2026 Posts: 4114 Rating:
|
follow up question published by Rashokis split to a seperate thread with the subjectSFC13''s parameter RECORD - description of the 240 diagnostic bytes Best regards CS Moderator |
|