hello DocT, it's the conductor capacitance that causes the above mentioned behaviour. The attached report describes this subject. The also attached catalog page shows a 3RT1916-1GA00 ''additional-load'' module. This module contains a resistor 22 kiloOhm and can be plugged into a 3RH1122-1AP00 contactor relay. Not knowing the actual conductor capacitance we are unable to guarantee that this accessory will help, but there is a good chance that it does. AttachmentD:\report on long cable runs.pdf (401 Downloads) |