(0)| 6/3/2014 4:49 PM | |
|
Posts: 14 Rating:
|
Dear all. I wonder if the repair 3RT1945-5AN21 COIL FOR Contactors is suitable for contactor 3RT1647 1AN21-capacitor AC CONTACTOR SW-6. tks. |
| 6/5/2014 8:17 PM | |
|
Posts: 14 Rating:
|
no fix for the contactor 3RT1647 1AN21? the manual says nothing about it. You can indicate which coil repair? tks. |
| 6/6/2014 2:12 PM | |
|
Posts: 14 Rating:
|
in the manual that I have, does not have information on coil. but need the order code. can you pass me the manual also. |
| 6/6/2014 2:39 PM | |
|
Posts: 4620 Rating:
|
Hello rafael-ws, Your coil code is not correct, you need 3RT1944-5AN21 220V,50Hz for 3RT1647 and the coil for 230V,50Hz if you want is 3RT1944-5AL21 I have in front of me the printed manual LV 2006 that can not find with google, if you wait a while I try to find it. Have a look: 3RT16 Capacitor contactors - Coil replacement - Siemens Industry ... |
Last edited by: Ste39 at: 6/6/2014 3:58 PMLast edited by: Ste39 at: 6/6/2014 3:55 PMLast edited by: Ste39 at: 6/6/2014 2:41 PM |
|