Hello Have you already seen this: Here an example, instead of SINAMICS you are using MICROMASTER - Connecting a SINAMICS drive to an S7-1200 CPU in TIA Portal (via GSD file) or SINAMICS Application Examples - Automation Technology - Siemens sorry but I do not use yet Tia Portal to communicate with MM4 via Profibus |
Last edited by: Ste39 at: 7/18/2014 4:47 PM |
|
| 7/18/2014 5:39 PM | |
|
Joined: 8/31/2005 Last visit: 12/16/2025 Posts: 2198 Rating:
|
He has a CPU317 and a MM4 in TIAP V12 (The S7-1200 is justan other Slave to the CPU 317) |
Last edited by: miami at: 7/18/2014 5:40 PM |
|
| 7/18/2014 8:57 PM | |
|
Joined: 7/13/2011 Last visit: 7/4/2025 Posts: 11 Rating:
|
Thanks to all, for yours response Attachment, yo will see my two projects, one of then was created in STEP 7 V5.5, and the other was created on TIA PORTAL V12. Rarely, in the step 7 works very well, but in TIA PORTAL V12 +sp1 Cant send or recerive data from my MM420. Thank you four your response Best Regards AttachmentS7300_MM420_PROFIBUS_TIA_V12.docx.pdf (1190 Downloads) |
| 7/21/2014 10:40 AM | |
|
Joined: 8/31/2005 Last visit: 12/16/2025 Posts: 2198 Rating:
|
For the communication with your MM, you selected PPO1 (6 Words). But you use SFC14/15 to transmit one word each. AttachmentD:\Process_Data_SFC.pdf (868 Downloads) |
|
|
|