Hello, maybe the DB1 is incompatible from 100U to 95U. Try to load the program without DB1 after clear PLC. Regards André Räppel --------------------------------------------------------------------------------- www.raeppel.de
work faster withinnovative PLC-Tools |
Last edited by: sps-concept at: 9/10/2014 7:32 AM |
|
This contribution was helpful to
|
|
| 9/11/2014 11:56 PM | |
|
Posts: 3 Rating:
|
Both of you guys, thank you very much. I did exactly what sps-concept said, DB1 was the main and unique error. After remove DB1, the PLC started to restart, and back to run normaly. Thank you very much. I really apreciate the help. Regards. Michael Rodrigues.