Please I need to know how to configure the TIA Portal V12 control via Profibus DP using a ET200S with Danfoss Drives , how to send the values of release , starting and stopping and also the references to speed, I am sending herewith the configuration I'm doing. Please help me AttachmentLP1.zip (184 Downloads) |
Last edited by: Min_Moderator at: 12/10/2014 11:14 AMChange text format |
|
12/6/2014 3:14 PM | |
Joined: 9/27/2006 Last visit: 9/20/2025 Posts: 12417 Rating:
|
Hello Martins; Profibus does not allow bit-level transfers. To change a bit value in (for example) PQW256, you must send a new word value, preferably in HEX. There was a discussion onthe forum recently that might help you: Programming profibus - Siemens Industry Online Support Hope this helps, Daniel Chartier |