(2)| 4/15/2015 7:25 AM | |
|
Posts: 719 Rating:
|
Does the reading change when applying a lower current value? (e.g. 5mA) |
| 4/16/2015 9:55 AM | |
|
Joined: 10/31/2014 Last visit: 8/20/2025 Posts: 66 Rating:
|
dear sir, Reading not change if mA change count is stable as always. |
| 4/16/2015 10:10 AM | |
|
Posts: 719 Rating:
|
You certainly have wrong connection on your module. You selected 4-20mA and you connected a potentiometer. (This is wrong) You need to connect the field correctly to your module (see attachment) Attachment2 AI I 2-4WIRE HF analog electronic module (6ES7134-4MB02-0AB0) - Connecting measuring sensors.pdf (292 Downloads) |
Last edited by: AMAZINGAHMED at: 4/16/2015 10:16:48 AM |
|
| 4/18/2015 5:47 PM | |
|
Joined: 10/31/2014 Last visit: 8/20/2025 Posts: 66 Rating:
|
ok sIR,,, i will try it ...
|