(0)| 5/15/2015 8:53 AM | |
|
Posts: 5 Rating:
|
Hi eisenpferdreiter, Simulating it works as you instructed, but the step does not wait until the block that is call to finish. It jumps to the next steps and so on. However, I found this https://support.industry.siemens.com/cs/mdm/54430386?c=35004217099&lc=en-US And works on the simulator, I haven't had the chance to try it on the machines yet but looks very promissing. Kind Regards, Billy |
| 5/15/2015 9:44 AM | |
|
Posts: 1058 Rating:
|
Hi Billy, yes, the step will not wait, as %M0.5 will immediately be set by ENO. When you start FB1 it will for sure take more than just one cycle till the homing is done. But the ENO will be set immediately when FB1 is completed in first cycle. Thus ENO will come way too soon for using it as condiion for transition 3. You should set %M0.5 when homing linear axis is really done and not by ENO. regards
|
| 5/15/2015 12:02 PM | |
|
Posts: 5 Rating:
|
Hi eisenpferdreiter, I have actually tried that before, but it seems that it can only do one cycle then again jumps around. Even though I have reset and set the BITS correctly. Hopefully, when I can download my current program to the PLC every thing works. I'll update you soon. Thank you for your help. Kind Regards, Bill |