Has anyone found a solution to the problem in TIA13 SCL where statements like "DB Item Force".DW[Valve_Index] := 9; // 9 = Force reset now no longer works in TIA, but used to work fine in Step7.
---------------------------------------------------------------------------------------------------- |
Last edited by: Min_Moderator at: 7/2/2015 4:03:43 PMNew subject after splitting |
|
| 7/2/2015 4:11 PM | |
|
Posts: 5225 Rating:
|
There are changes between Step7 V5.x and Step7 V1x. w |
Last edited by: William_B at: 7/2/2015 4:13:46 PMadd link #2 |
|
This contribution was helpful to
|
|
| 7/2/2015 4:15 PM | |
|
Posts: 5 Rating:
|
After a bit of searching I found that the equivalent in TIA 13 is :- WORD_TO_BLOCK_DB(355).DW(#Valve_Index) := 9; Tested with PLCSIM...seems to work OK. :) |