(0)| 7/21/2015 11:20 AM | |
|
Posts: 9 Rating:
|
Hello, had same problem, reason the DB tags of PID v2.2 different from V1.2. I corrected SCL code for working with V2.2. Just replace SCL code from FB670 with code from file it should work, except limits for input and output it still will be setted by default FB670 value eg 0.0 to 27648.0 for input and 0.0 to 100.0 for output. For more information check comments in code. AttachmentFB670_by_max.txt (90 Downloads) |
This contribution was helpful to
|
|
| 7/21/2015 2:27 PM | |
|
Posts: 9 Rating:
|
By the way, sombody have WinCC 7.2/7.3 faceplate for FB670? |