(1)| 11/3/2015 3:24 PM | |
|
Posts: 120 Rating:
|
hello i have problem, i need connect sensor 4-20 mA to LOGO8 with AM2, what perametr i must set if i wanna that 4 mA is zero and 20 mA is 100 %, |
| 11/3/2015 3:46 PM | |
|
Joined: 12/18/2014 Last visit: 1/18/2026 Posts: 36472 Rating:
|
Look at attachment. |
| 11/3/2015 3:55 PM | |
|
Posts: 120 Rating:
|
i try it of 4 mA i get 0 % but in 6mA i have 100 |
| 11/3/2015 6:29 PM | |
|
Joined: 12/18/2014 Last visit: 1/18/2026 Posts: 36472 Rating:
|
Here is the file, for example.
AttachmentSchaltplan1.zip (292 Downloads) |
| 11/4/2015 7:32 AM | |
|
Joined: 2/12/2014 Last visit: 11/6/2025 Posts: 158 Rating:
|
is the value whne you inject 6mA maximum? |
| 11/4/2015 4:37 PM | |
|
Joined: 12/18/2014 Last visit: 1/18/2026 Posts: 36472 Rating:
|
Here's a little more Information.
AttachmentLogo overview analog voltage current units.pdf (360 Downloads) |