Hello, a upload of HMI device is only possible if the option "backtransfer" was activated during the download. If this was not then you can't upload anything from the Panel. The only thing you cvan do then is a Backuo/restore with Prosave to transfer the HMI Data from the Panel to another Panel (same Type). Check this FAQ's for how to do it: How do you back transfer the projects of an operator panel and what should you watch out for? How do you backup/restore with a Windows-based panel? Regards |