Hello, ET200S Manual Capter 3.2 https://support.industry.siemens.com/cs/de/en/view/12490437 If ypu have a RED SF LED on the PLC is very good if you take a look in the diagnostic buffer of the PLC, here ypu get information which error is present.
Christoph |
This contribution was helpful to
|
|
| 2/11/2016 3:00 PM | |
|
Posts: 767 Rating:
|
Thanks, the DIP switch setting was different in Hardware configuration and the module. Cheers, |