Hello I have problem with ASI IO modules, they are going error state for a second, and that causes line stoppage. Have anyone some idea what could cause this error. I think problem is in one or maybe two faulty modules. But how to find faulty module, I have 39 IO modules on two lines. and both lines go for error state as you can see in this video https://www.youtube.com/watch?v=jevQP9jO2Lk&feature=youtu.be |
| 3/11/2016 2:48 PM | |
|
Posts: 63 Rating:
|
ithik you have a little bit short circuit in your asi network or some junction is loose if you have a brand new asi master you can take a look on its LCD , it say you wich address has problem otherwise you can check your asi network with asi interface control tools software from bihl+wiedemann company that can give you a good overview from your asi network and tell you wich slave is not correct and a lot of other options . Attachmentbihl and wiedemann bw1602.pdf (396 Downloads) |