9/16/2010 5:05 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating:
|
Kreso, Why do you have to add them to HW Config? Regards, Behnam www.sigmaprocess.ca/blog |
9/16/2010 6:28 PM | |
Joined: 9/15/2010 Last visit: 6/30/2025 Posts: 27 Rating:
|
![]() ![]() Tnx for replying! The reason why I want to add them in HW is so I can have them in DP diagnostic. CPU type that I am useing is 414-3 DP. Please check in attachment properties of the CPU and set properties for profibus line on which I connected OP's. Strange thing is that with one OP in HW it works and I get profibus fault when I unplug the line from OP, but with more then one OP in HW I dont have connection with OP's any more. Regards! AttachmentCPU 414-3 DP.zip (252 Downloads) |
9/16/2010 9:58 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating:
|
Kreso, If you would like to know whether the HMI is communicating with CPU, you better use the "Life Bit" in the "Coordination Area Pointer" in Wincc Flex. Please take a look at theattached file. Regards, Behnam www.sigmaprocess.ca/blog AttachmentCoordination-Life Bit.pdf (379 Downloads) |
This contribution was helpful to
1 thankful Users |
9/20/2010 7:46 PM | |
Joined: 9/15/2010 Last visit: 6/30/2025 Posts: 27 Rating:
|
Hi Behnam, Thank you for replaying, life bit solved my problem. I have my diagnostic now :-). Best Regards! |
3/28/2016 1:11 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4760 Rating:
|
New question published by ALPHA_1 is split to a separate thread with the subject Transfer project to MP277 by WinCC flexible. Best regards |