(0)| 5/3/2016 9:45 PM | |
|
Posts: 3 Rating:
|
Is it shown as an arrow, for example? The client wants to know whether the current is going "upwards" or "downwards". Thank you. |
| 5/3/2016 10:46 PM | |
|
Joined: 12/4/2009 Last visit: 11/6/2025 Posts: 453 Rating:
|
.TT, I suppose your client wants to see arrows for positive/negative power direction. I don't think that's possible with PAC3200. If my memory serves me well, you have a button to exchange Import/Export power values on the screen, and also minus sign for negative direction. From PAC3200 manual: "Please take account of the direction of current flow when connecting the current measuring inputs. With inverse connection, the measured values are inverted and receive a negative sign." Manual SENTRON Power Monitoring Device PAC3200 Regards. |
Last edited by: crazyCow at: 5/3/2016 10:50:38 PMIf this post actually helped, you may consider using the Rate button above. |
|
This contribution was helpful to
|
|
| 5/4/2016 1:34 PM | |
|
Posts: 3 Rating:
|
crazyCow, It has certainly helped me. Thanks a lot! |