I have problem to understand MCCB 3VL invesre delay time (L) for breaker3VL ETU22 . I have not referance or curve to account time ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 5/27/2016 12:10:04 PMNew subject after splitting |
|
| 5/26/2016 7:00 AM | |
|
Posts: 8092 Rating:
|
Please refer the attached sheet. This chart helps to understand different setting parameters of ETU for overload, short circuit & instantaneous short circuit protections. Depending upon operating current & MCCB location in power line stream user needs to set those parameters. HTH. AttachmentSENTRON_3VL MCCB parameter setting curves.pdf (403 Downloads) |