(1)| 6/22/2016 2:07 PM | |
|
Posts: 8092 Rating:
|
Is it 4Q or 1Q drive? Have you carried out speed optimization satisfactorily? Check the torque limit value at p50169. HTH. |
| 6/22/2016 5:08 PM | |
|
Posts: 46 Rating:
|
I just have noticed that in diagnostic, when it starts decelerating it says "o0.0 no torque sense conected" |
| 6/23/2016 6:59 AM | |
|
Posts: 8092 Rating:
|
During commissioning have you selected the correct MLFB number of drive i.e. size of unit 2Q? Please check & confirm. |
| 6/23/2016 10:59 AM | |
|
Joined: 8/25/2006 Last visit: 1/14/2026 Posts: 2221 Rating:
|
Hello. In 2Q drive negative current limit is always 0% or higher (function diagram 6840). You should use braking with field reversal. |
This contribution was helpful to
|
|
| 6/23/2016 11:06 AM | |
|
Posts: 46 Rating:
|
Hi So i should make it changing P50581[0]??? And which "r" should I put? I haven´t got it clear |
Last edited by: jmlai at: 6/23/2016 11:23:06 AM |
|