(0)| 1/19/2016 1:25 AM | |
|
Joined: 10/7/2005 Last visit: 1/16/2026 Posts: 3054 Rating:
|
Hello PANNI Profibus DP is Profibus DP and independent of the DP Master in use (be it an S7-300 or S7-400 or any other DP Master). Presuming you use cyclic I/O's between the DP Master and your third party (TP) device, the TP will get the values every Profibus DP scan (again, irrespective if it is an S7-300 or S7-400 or any other DP Master). As such I am not too sure yet where your problem lies, but if you can provide more details about your setup, TP device and S7 program in use, I am confident we can work out what is going on (or going wrong). |
|
Cheers |
|
This contribution was helpful to
|
|
| 1/19/2016 8:27 AM | |
|
Posts: 34 Rating:
|
Thank you Fritz for your prompt response, As you asked I have attached herewith the cfg files and DP write program snaps for both 300 and 400 CPU. Here TP devices are feeder system controllers. PLC programming and DP communication settings for both to CPUs are identical as i attached. Kindly have a look and let me know what is the limitation with 300 CPU for the issue. Thanks and Regards, Attachment300 - 400.rar (253 Downloads) |
| 1/20/2016 4:22 AM | |
|
Joined: 10/7/2005 Last visit: 1/16/2026 Posts: 3054 Rating:
|
Hello PANNI ok, nothing obvious seems to be wrong with your config, so here are few more questions and pointers: 1.) Do you use the one and only same physical TP for the S7-300 and 400 test? Since your TP Profibus DP Slave Interface is based on an Anybus device, it would require some configuration and should your S7-400 and S7-300 each have their own TP, the two TP's may differ in their config and this could be the cause for your problem. 2.) Is your S7-300 really a 315-2AH14 as per the cfg files that you uploaded? Older S7-300's had a limit of supporting max 32 Bytes of consistent Profibus DP I/O data and your config is set up for 80 Bytes (I doubt this is the reason for your problem, but worthwhile a quick check anyhow) 3). As a test, can you expand your S7-300 Process Image size to include your TP I/O's. Thereafter get rid of SFC15 and write directly all TP Outputs (e.g. T QD 728; T QD 732 etc.) |
|
Cheers |
|
| 7/21/2016 12:45 PM | |
|
Posts: 34 Rating:
|
Hello Fritz.. Please help. The problem is still as it is. Awaiting your comment if any clue to resolve the issue. Regards. |