Hello, perhaps it refers to this: |
|
This contribution was helpful to
|
||
| 9/25/2016 11:13 PM | |
|
Posts: 116 Rating:
|
Hello Ste39, Thanks for your reply. But 1-
How can we check this point in the program for Ethernet,Profinet,Profibus,.......communication? 2-
Please explain this point? 3-Kindly check the following result: We can replace the inverter to another brand without modifying PLC program if: No device ID and No vendor ID in the PLC program and the telegram is similar. Best regards..... |
| 9/29/2016 7:04 AM | |
|
Joined: 5/12/2006 Last visit: 1/16/2026 Posts: 22827 Rating:
|
Hello, the check for Vendor/Device ID is in the FW of the PLC, you can't disable such feature because is FW and not USEr PLC Program.
Christoph |