(0)| 1/7/2017 7:23 PM | |
|
Posts: 10 Rating:
|
Hi all, Can you tell me what is the problem and solution if the diagnostic buffer event is alignment error when writing/reading? |
| 1/7/2017 7:39 PM | |
|
Posts: 4620 Rating:
|
Hello, https://support.industry.siemens.com/tf/ww/en/post/613134/ perhaps if you share to us your diagnostic buffer may help you |
| 1/8/2017 8:23 AM | |
|
Posts: 10 Rating:
|
This is the error |
| 1/8/2017 8:52 AM | |
|
Posts: 10 Rating:
|
Hi, How do I search? |
Last edited by: fedfp03 at: 1/9/2017 7:20:02 AM |
|
| 1/8/2017 9:21 AM | |
|
Posts: 10 Rating:
|
It is not called in any OB |
| 1/8/2017 9:30 AM | |
|
Posts: 623 Rating:
|
Hi fedfp03, This is error due to indirect addressing. 1. You have to test FC individually with some arbitrary input paranmeters. Ascertain valid limits of input parameters. 2. If it's ok, then check how various inputs are transferred and they are within limits. |
| 1/10/2017 4:46 AM | |
|
Posts: 10 Rating:
|
Thank you all for your response. We replace the CPU and now its ok. |