(2)| 1/13/2017 5:48 AM | |
|
Joined: 12/18/2014 Last visit: 1/17/2026 Posts: 36470 Rating:
|
Yes that is possible. See attachment. When you connect the potentiometer to I7, the analogue input is AI1. Need you an example of the LOGO! curcuit? AttachmentLOGO! 8 Soft manual 0BA8 2014_06 page 43.pdf (324 Downloads) |
This contribution was helpful to
|
|
| 1/13/2017 7:49 AM | |
|
Joined: 12/18/2014 Last visit: 1/17/2026 Posts: 36470 Rating:
|
You don't require a 6.6 kOhm potentiometer, but a 5 kOhm potentiometer and a 6.6 kOhm series resistor to the potentiometer. In this example is the maximim timer value 1000s (= 16m40s). AttachmentTimer_value_over_analogue_input.zip (307 Downloads) |
This contribution was helpful to
|
|