(0)| 5/1/2017 12:31 PM | |
|
Joined: 12/27/2006 Last visit: 11/17/2025 Posts: 1200 Rating:
|
This is a begin. Notice that the LOGO works analog intern wit 0-1000 for a 0-10V signal Difference 15 to 45 degrees = 30 degrees. Look in the mathematical block for the calqulations AttachmentSchakelschema1.zip (241 Downloads) |
Last edited by: Toeternietoe at: 5/1/2017 12:31:52 PM |
|
| 5/1/2017 2:36 PM | |
|
Joined: 12/18/2014 Last visit: 1/19/2026 Posts: 36484 Rating:
|
Here a possible solution. The temperature area from 15.0 °C - 45.0 °C converts to 0-1000 Units and so on the analog output 0-10V.
AttachmentLimited_temp_to_0-10V_output_0BA8.Standard.zip (252 Downloads) |
This contribution was helpful to
|
|
| 5/1/2017 3:06 PM | |
|
Posts: 3 Rating:
|
Hi ixo65 & toeternietoe, many thanks for the proposed solutions. Got these both tested out now and so have two working scenarios. Again many thanks |