(0)| 5/28/2008 1:56 PM | |
|
Posts: 2348 Rating:
|
There would be temperature in 0.1°C. So you just divide code by 10 to get temperature. |
| 5/29/2008 8:10 AM | |
|
Posts: 289 Rating:
|
So when I choose U or I then I will get 0 to 32767 ? Thank you all. |
| 5/29/2008 8:29 AM | |
|
Joined: 9/27/2006 Last visit: 1/13/2026 Posts: 12480 Rating:
|
Hello ionut.b; No, it is slightly more complex than that. You should take a few minutes to read the chapter on Analog Value Representation in the following S7-300 module Data manual: http://support.automation.siemens.com/WW/view/en/8859629 Examine especiallythe tables that rre used in that chapter, they shouls answer most of your questions. You can come back to us if something is not quite clear, of course. Siemens has created 2 standard blocks, FC105 (SCALE)and FC 106 (UNSCALE) that you can use to move data from an analog input to a REAL value in your program in engineering values, and from a REAL: value to an analog output. You will find them in the TI-S7 converting blocks library. Hope this helps, Daniel Chartier |
This contribution was helpful to
|
|
| 5/29/2008 8:44 AM | |
|
Posts: 289 Rating:
|
Thank you dchartier for the link. I will go through it I have used FC105 for scaling analog values, bu never used a module for PT100. |
| 5/29/2008 10:03 AM | |
|
Posts: 289 Rating:
|
Great, thank you very much. |