* Thank you for Reply * Seven Segment Display are Show 6# find the attached jpg. |
2/8/2018 5:39 AM | |
Joined: 4/23/2010 Last visit: 11/14/2024 Posts: 8092 Rating: (878)
|
You did not replied NCU MLFB number. However, please check the RDY LED status, is it steady or flashing? Please refer the attached sheet, will help you to identify the problem. Further more, please check the fans on 840D module. Is it running? HTH. Attachment840D SL 7 segment booting display status.pdf (147 Downloads) |
2/12/2018 10:19 AM | |
Posts: 24 Rating: (0) |
Plz Help and Suggest any Expert Person. find the Problem . ?? |
2/13/2018 4:52 AM | |
Joined: 4/23/2010 Last visit: 11/14/2024 Posts: 8092 Rating: (878)
|
Hello 1122WAqar, From last one week the same problem is on your machine & the alarm message indicates it is communication problem i.e. machine drive communication has failed. Check the profibus connectors, wire from NCU to drives. In previous post description & snaps, contradictory information is provided which is not sufficient. If every thing is ok, you need to go on line & check the problem. So instead of this I suggest you to get help from Siemens support center. HTH |