hi StamGuy, current measuring 2-wire and PT100-measuring are two totally different measurements. Your module 6ES7134-4GD00-0AB0 can only work with 2-wire-transducer. If you have a PT100-sensor you need to use a RTD-module, like 6ES7134-4JB51-0AB0 hope this helps, regards, |
| 5/17/2018 2:03 PM | |
|
Joined: 3/20/2017 Last visit: 1/19/2026 Posts: 145 Rating:
|
I have a transducer with the PT100 so I get a 4-20mA signal |
| 5/21/2018 11:54 AM | |
|
Joined: 3/20/2017 Last visit: 1/19/2026 Posts: 145 Rating:
|
Here is the data sheet of the device
AttachmentTP100.pdf (266 Downloads) |