Hello, if you just want to control the drive by enabling it and giving a speed setpoint I would do the whole control via PLC with standard telegram 1 and SINA_SPEED function block for PLC. The block is part of the DriveLib, which is installed to TIA automatically when Startdrive package is installed. Otherwise you can download the library here: https://support.industry.siemens.com/cs/ww/en/view/109475044 I think this is the easiest way to begin with the communication and the drive functions. |