What happened if i changed P350? My motor full load current is 8.4amp, at parameter P350 the value is 8.4, so i am not getting output value more than this in case it goes higher from this. Please suggest me how i will get output more from it.
------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 9/26/2018 2:48:39 PMNew subject after splitting |
|
| 9/28/2018 6:20 AM | |
|
Posts: 8092 Rating:
|
If you increase P350 value i.e. motor rated current value, its danger to motor, will damage/fail. Why you want to increase it? |