hi all in my factory one master-islave DP communication is used in one plant.(slave is s7-300 and master is s7-400). this system works correctly and master reads information from slave without any problem. i opened their projects and I was faced with a strange thing in configuration. in slave ,configuration i/o addresses are different from i/o addresses in master..and program for transfering data that is writed in slave is corresponding with slave configuration and no corresponding with master configuration.. my ask is how does this system work correctly? please see attached pictures . thank you Attachmentplc.zip (234 Downloads) |
| 9/29/2018 3:34 PM | |
|
Joined: 9/27/2006 Last visit: 1/16/2026 Posts: 12481 Rating:
|
Hello a.z.r.; In most exemples you will find on Siemens' support, the situation is simplified and input/output addresses are the same. For example: https://support.industry.siemens.com/cs/ww/en/view/6518822 But this similarity in addressing is not mandatory, you can select any addresses as available in your CPUs as long as they respect size and consistency requirements for your application. Hope this helps, Daniel Chartier
|