(0)| 11/25/2018 1:54 PM | |
|
Joined: 3/30/2011 Last visit: 1/18/2026 Posts: 740 Rating:
|
Hello, how many slave do you have? length of the network? speed? did you check termination resistor? If the 440 node is at the end of the network please see this thread Best Regards |
Last edited by: mindware at: 11/25/2018 1:55:37 PM★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★ |
|
| 11/26/2018 10:59 AM | |
|
Posts: 80 Rating:
|
I did it but again the same |
| 11/26/2018 11:08 AM | |
|
Posts: 5521 Rating:
|
hi muha_mag, sounds like you have problems in wiring, grounding or shielding. On the first and the last node of a Profibus line you need to acitvate a termination(resistor)). Check also if your devices have a proper grounding and if the shield of your PB-wires is proper grounded. hope this helps, regards, |
| 11/30/2018 8:25 AM | |
|
Posts: 80 Rating:
|
the problem was to ground thank you
|