(1)| 1/26/2019 8:16 AM | |
|
Posts: 51 Rating:
|
HI ANY ONE CAN SUGGEST RING COUNTER MODULE IN LOGO COMFORT 0BA8 |
| 1/26/2019 8:21 AM | |
|
Joined: 12/18/2014 Last visit: 1/19/2026 Posts: 36482 Rating:
|
The term "RING COUNTER MODULE" does not mean anything to me. Can you explain what you mean by that? |
| 1/26/2019 8:39 AM | |
|
Posts: 51 Rating:
|
HI THERE IS 3 PUMPS, EACH WEEK PUMP SHOULD BE CHANGE OVER AS LIKE BELOW 1ST WEEK P1 & P2 2ND WEEK P2 & P3 3RD WEEK P3 & P1 4TH WEEK P1 & P2 |
| 1/26/2019 8:52 AM | |
|
Joined: 12/18/2014 Last visit: 1/19/2026 Posts: 36482 Rating:
|
You've already asked for something like this in this topic, https://support.industry.siemens.com/tf/de/en/posts/change-over-logic/178537/?page=0&pageSize=10 but you just called your question different. Was the forum search function not helpful? |
| 1/26/2019 9:27 AM | |
|
Joined: 12/18/2014 Last visit: 1/19/2026 Posts: 36482 Rating:
|
Here's a simple example.
AttachmentWeekly_changing_pump_priority_0BA8.Standard.zip (313 Downloads) |
This contribution was helpful to
|
|
| 1/26/2019 9:31 AM | |
|
Posts: 51 Rating:
|
i couldn't found what my expectation. if you can do one favor please. i have logic which is change over for 2 fan if you can edit on that logic for 3 fan more fan. the logic should be 1 & 2 2 & 3 3 & 1
Attachmentduty change over FAN.zip (313 Downloads) |
| 1/26/2019 5:38 PM | |
|
Posts: 2826 Rating:
|
That makes a good solution for this question. |