Hello friends if I just want to read high speed input using s71214c plc then can I use notation ":P" with high speed input in OB1 or I have to use HSC for these input ?? Thanks in advance ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 2/27/2019 1:31:18 PMNew subject after splitting |
|
| 2/27/2019 12:27 PM | |
|
Posts: 5521 Rating:
|
hi, It depends on what you want to do with this input. In S7-1200 system-manual you find all supported applications regarding the HSC on the S7-1200. SIMATIC S7 S7-1200 Programmable controller just to use ":P" is only a direct access to the perphery. You don´t know what happens between two accesses. I guess you rather need a process-alarm. When the input gets high, a process-alarm-OB will be called and you can react to this input inside this OB. hope this helps, regards, |
| 2/28/2019 7:20 AM | |
|
Posts: 3 Rating:
|
Thanks, Its actually single pulse only I will try by Pulse catch Thanks again |