3/15/2019 8:04 AM | |
Joined: 11/5/2012 Last visit: 8/14/2025 Posts: 490 Rating:
|
Oh sorry, we are using sinumerik 840d solution line. PCU50 ...sent from App |
3/15/2019 4:16 PM | |
Joined: 5/24/2016 Last visit: 9/11/2025 Posts: 412 Rating:
|
Hello Rescobedeo That is not a problem. If you set the password to Manufacture level. Then if you go to the Program manager and choose the directory you want to hide, then mark it and go to "Properties" in the Vertical softkeys. There you have the option to set different access levels for the following 4 operations Execute Write List Read You then want to change the List access right. I have added a small video clip where I do it in Sinutrain Best Regards Riddersholm AttachmentRights setting - Program Manager.avi (120 Downloads) |
This contribution was helpful to
3 thankful Users |
3/22/2019 4:40 AM | |
Joined: 11/5/2012 Last visit: 8/14/2025 Posts: 490 Rating:
|
Hello, thanks so much. I didn't see the "list" option, Now its all the way the plant wants it. thanks again. Regards. |