(2)| 4/16/2019 8:48 AM | |
|
Joined: 12/18/2014 Last visit: 1/17/2026 Posts: 36469 Rating:
|
Make a second level, e.g. 3.0 m. Need you an example? |
| 4/16/2019 8:54 AM | |
|
Posts: 15 Rating:
|
If you have an example I'll be happy |
| 4/16/2019 9:01 AM | |
|
Joined: 12/18/2014 Last visit: 1/17/2026 Posts: 36469 Rating:
|
Do you have any inputs which indicate faults of the pumps? Then you could switch the pumps in case of failure. |
| 4/16/2019 9:42 AM | |
|
Joined: 12/18/2014 Last visit: 1/17/2026 Posts: 36469 Rating:
|
Here's an example for a LOGO! 0BA8.Standard.
AttachmentPump_control_by-fill_level_0BA8.Standard.zip (465 Downloads) |
This contribution was helpful to
|
|
| 4/16/2019 11:49 AM | |
|
Posts: 15 Rating:
|
Tanks, :-) |