Hello, After a few weeks of the attached program running, a small problem has come to light. the machine stop part of the program has a count for number of stops and a timer made up of hours, minutes and seconds recording the elapsed time. Although the machine stop part of the program works flawlessly in a logo simulation offline.In a running and live state the actual number of stops does not increment singularly for example I4 is activated and the counter displays 4 as the number of stops whilst the machine has only stopped once and if the machine is stopped for a second time the counter could display 10 it seems purely random.But the counter works fine during a offline simulation. at this moment in time i am totally baffled, so i would be grateful for some pointers in clearing this matter up Ade AttachmentInverter_Speed_Preset_ACM2_v3.1_Gain1.0.zip (291 Downloads) |
| 5/13/2019 9:44 PM | |
|
Posts: 87 Rating:
|
I have a logo 8 standard capable of 4hz according to the manual, I'll try the on-off delay block thank you for you time ade |
| 5/13/2019 10:06 PM | |
|
Posts: 87 Rating:
|
LOGO BM 24 RCE:- 6ED 1052-1HB00-0BA8 |
| 5/13/2019 10:11 PM | |
|
Joined: 12/18/2014 Last visit: 1/17/2026 Posts: 36470 Rating:
|
This LOGO! has no fast count inputs. Then must the On-/Off Delay solve your problem, I think. |
| 5/13/2019 10:17 PM | |
|
Posts: 87 Rating:
|
thank you. I will post back if I win lose or draw with you solution once again thank you for your time |