(0)| 6/10/2019 8:37 AM | |
|
Posts: 623 Rating:
|
Hi keefor, U just need to modify hardware configuration. There are multiple ways but see below mine one- 1. Create H project: Create new project. Insert H station. Drag both CPU. Add manually all existing modules & keep addresses identical. Compile & Save. U can refer installed manual 'Fault tolerant system' available in Siemens -documentation. Compile all in Net -pro also if possible. 2. Open Old project . Copy all blocks except system data from old to new project. Copy symbols table, source files if any to new project. 3. In new project- Check block consistency (compile all). Note- It's better if u could replace S7 timers with IEC block or own timer blocks in logic. |
This contribution was helpful to
|
|
| 6/10/2019 5:17 PM | |
|
Posts: 2 Rating:
|
Thank you! I will try to go this way. |