Dear all, Actually i want to know what are the ways to connect standalone profibus slaves like drives, sensors etc in H system. |
| 1/10/2020 7:22 PM | |
|
Joined: 9/27/2006 Last visit: 1/16/2026 Posts: 12481 Rating:
|
Hello sarathcrsp; To connect a redundant H-system to single-onterface Profibus slaves, you need a Y-link: How is the Y-link structured ? https://support.industry.siemens.com/cs/us/en/view/43688632 Here is the manual for the Y-link: https://support.industry.siemens.com/cs/us/en/view/1142696
Hope this helps, |