Dear Experts and Users I create input CH 0 (assume encoder connect to CH0) increase by second. Then i can see that PV1 display the number that CH0 had enven though SwGateEn = 0 (i didn't use HwGate in config). And when i try to turn ON/OFF SwGateEn or StopGate the value in PV1 also same with input CH0. My questions are: Do i make something wrong or i have to have real hardware to test this function ? Thanks you for your attention and sharing. (Attached is what i configured for counter CH0) ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 01/09/2020 16:43:28New subject after splitting |
|
| 1/29/2020 5:16 PM | |
|
Joined: 9/3/2013 Last visit: 1/2/2026 Posts: 152 Rating:
|
See: https://support.industry.siemens.com/cs/de/en/view/109760968 chapter : 16.15 -> You need real Hardware to test this function's. There is some communication behind the scene between FM350-2 and Cnt blocks. Regards |